| Three common serial data standards,
RS-232, RS-422, and RS-485, are described by
specification and electrical interface. Cable
termination techniques, use of multiple loads,
daisy-chaining of RS-232, conversion of RS-232
to RS-485, conversion of RS-485 to RS-232, and
RS-232 port-powered RS-485 conversions are
described.
Introduction"The great thing about
standards is there are so many to choose from."
This statement was made at a recent conference
on fiber optics, and it holds true for
electrical-interface standards as well. As
serial-data standards tend to evolve separately
within particular industries, we thus have more
standards than we should.
Perhaps the most successful serial-data
standard for PC and telecom applications is the
RS-232. Similarly, the RS-485 and RS-422 are
among the most successful standards for
industrial applications. These standards are not
directly compatible. For control and
instrumentation applications, however, it is
often necessary to communicate between the
standards. This article discusses the different
standards (electrical physical-layer
specifications), explains how to convert from
one standard to another standard, and
demonstrates how to combine different standards
within the same application.
RS-232 Electrical Specifications and a
Typical ConnectionThe RS-232 link was
initially intended to support modem and printer
applications on IBM PCs, however, it now enables
a variety of peripherals to communicate with
PCs. The RS-232 standard was defined as a
single-ended standard for increasing
serial-communication distances at low baud rates
(<20kbps). Over the years the standard
changed to accommodate faster drivers like the
MAX3225E, which offers 1Mbps data-rate
capability. For RS-232 compliance, a transceiver
such as the MAX3225E must meet the electrical
specifications listed in Table 1. A
typical connection (Figure 1) shows the
use of hardware handshaking to control the flow
of data.
Table 1. RS-232 Summary of Major
Electrical Specifications
| Parameter |
Conditions |
Min |
Max |
Units |
| Driver Output Voltage, Open Circuit |
|
|
25 |
V |
| Driver Output Voltage, Loaded |
3k
< RL < 7k |
±5 |
±15 |
V |
| Driver Output Resistance, Power Off |
-2V < V < 2V |
|
300 |
|
| Slew Rate |
|
4 |
30 |
V/µS |
| Maximum Load Capacitance |
|
|
2500 |
pF |
| Receiver Input Resistance |
|
3 |
7 |
k |
| Receiver Input
Threshold: |
| Output = Mark (Logic 1) |
|
-3 |
|
V |
| Output = Space (Logic 0) |
|
|
3 |
V |
 Figure
1. Typical RS-232 connection.
A typical RS-232 signal (Figure 2,
CH1) swings positive and negative. Note the
relative location of the 0V trace markers on the
left axis. Although the RS-232 data is inverted,
an overall translation from TTL/CMOS to RS-232
and back to TTL/CMOS restores the data's
original polarity. Typical RS-232 transmissions
seldom exceed 100 feet for two reasons. Firstly,
the difference between transmitted levels (±5V)
and receive levels (±3V) allows only 2V of
common-mode rejection. Secondly, the distributed
capacitance of a longer cable can degrade slew
rates by exceeding the maximum specified load
(2500pF). Because the RS-232 was designed as a
point-to-point rather than multidrop interface,
its drivers are specified for single loads from
3k
to 7k .
Therefore, a daisy-chain scheme is typically
implemented for multidrop interface applications
(Figure 3).
 Figure
2. An RS-232 receiver accepts the bipolar input
signal (top trace, CH1) and outputs an inverted
TTL/CMOS signal (bottom trace, CH2).
 Figure
3. Daisy-chaining allows multiple slave
transceivers on a single RS-232 line.
Daisy-Chain Devices and Their
LimitationsIn a daisy-chain configuration,
the RS-232 signal enters through one receiver
and is looped through to a transmitter. This
configuration is repeated for subsequent devices
along the data transmission line. Cable breaks
are a major problem with this technique. A break
between slave 1 and slave 2 prevents all
downstream devices from transmitting or
receiving data. Other multidrop RS-232
techniques involve prebuffering or boosting the
RS-232 output drive (enabling it to drive
multiple 5k
inputs in parallel).
To eliminate the problems associated
daisy-chain networks, Maxim developed the
MAX3322E/MAX3323E, specifically designed to be
configured in multidrop applications. These
unique devices employ a logically switched input
resistance of 5k . When a device is not
selected, its input resistance remains in a high
impedance state allowing communication to
proceed with other devices along the shared bus.
Another solution to the daisy-chain network
problem is to convert the RS-232 Rx and Tx
signals to RS-422 signals (see Table 2).
RS-422 is a differential standard that allows
transmission over much greater distances. The
higher input resistance of RS-422 inputs,
combined with their higher drive capability,
allows a connection of up to ten nodes
(Figure 4). Another RS-422 advantage is
the separate transmit and receive paths for
which no direction control is needed. Any
necessary handshaking between devices can be
performed with either software (XON/OFF
handshaking) or hardware (a separate set of
twisted pairs). The MAX3162 provides an
economical way to translate between RS-232 and
RS-422 signals. For more detail about this
process, refer to the section below entitled
RS-232/RS-485 Protocol Translators.
Table 2. RS-422 Summary of Key
Specifications
| Parameter |
Conditions |
Min |
Max |
Units |
| Driver Output Voltage, Open Circuit |
|
|
±10 |
V |
| Driver Output Voltage, Loaded |
RL = 100 |
2 -2 |
|
V |
| Driver Output Resistance |
A to B |
|
100 |
 |
| Driver Output Short-Circuit Current |
Per output to common |
|
150 |
mA |
| Driver Output Rise Time |
RL = 100 |
|
10 |
% of bit width |
| Driver Common-Mode Voltage |
RL = 100 |
|
±3 |
V |
| Receiver Sensitivity |
VCM < ±7V |
|
±200 |
mV |
| Receiver Common-Mode Voltage Range |
|
-7 |
7 |
V |
| Receiver Input Resistance |
|
4 |
|
k |
| Differential Receiver Voltage |
Operational |
|
±10 |
V |
| Withstand |
|
±12 |
V |
 Figure
4. A typical RS-422 system allows as many as ten
slave transceivers on the differential
transmission line.
Differences Between RS-485 and RS-422 and
Their Use in ApplicationsRS-422 and RS-485
transceivers are often confused with each other;
one is assumed to be a full-duplex version of
the other. The electrical differences, however,
in their common-mode ranges and receiver-input
resistances make these standards suitable for
different applications. As RS-485 meets all the
RS-422 specifications (Table 3), RS-485
drivers can be used in RS-422 applications. The
opposite, however, is not true. The common-mode
output range for RS-485 drivers is -7V to +12V,
whereas the common-mode range for RS-422 drivers
is only ±3V. The minimum receiver-input
resistance is 4k
for RS-422 drivers and 12k
for RS-485 drivers.
Table 3. RS-485 Summary of Key
Specifications
| Parameter |
Conditions |
Min |
Max |
Units |
| Driver Output Voltage, Open Circuit |
|
1.5 -1.5 |
6 -6 |
V V |
| Driver Output Voltage, Loaded |
RL = 100 |
1.5 -1.5 |
5 -5 |
V V |
| Driver Output Short-Circuit Current |
Per output to common |
|
±250 |
mA |
| Driver Output Rise Time |
RL = 54 CL
= 50pF |
|
30 |
% of bit width |
| Driver Common-Mode Voltage |
RL = 54 |
|
±3 |
V |
| Receiver Sensitivity |
-7V < VCM < 12V |
|
±200 |
mV |
| Receiver Common-Mode Voltage Range |
|
-7 |
12 |
V |
| Receiver Input Resistance |
|
12 |
|
k | To
reduce wiring expense and achieve longer line
lengths, RS-485 transceivers have become a
popular standard for use in point-of-sale,
industrial, and telecom applications. The wider
common-mode range of RS-485 also enables longer
line lengths and a higher input resistance per
node, allowing more nodes to be connected to the
bus (Figure 5).
 Figure
5. Compared with RS-422, the higher input
impedance and wider common-mode range of an
RS-485 connection enables longer line
lengths.
Differential RS-485 transmissions (Figure
6) produce opposing currents and magnetic
fields along each segment (wire) of a
twisted-pair cable, thus minimizing the emitted
electromagnetic interference (EMI) by
cross-canceling the opposing fields around each
wire. For transmissions through a long cable or
at high data rates, the cable appears as a
transmission line and should be terminated with
the cable's characteristic impedance. This
aspect of the RS-485 connection causes
confusion. Does the line need to be terminated,
and if so, how should it be terminated? If the
designer is not the end user, should these
questions be left for the installer to resolve?
For most RS-485 transceivers, the data sheet
indicates a simple choice between no termination
and a simple point-to-point termination when the
cable acts as a transmission line (Figure
7). A termination resistor across the A-B
terminals is harmless. By default, the
transmission line should be terminated at the
last transceiver on the line (bus).
 Figure
6. The opposite polarity signals on an RS-485
line minimize EMI by cross-canceling each
other's respective magnetic fields. The GND
references on the above scope photo have been
shifted (offset) to clearly show the inverted
polarities of the RS-485 output signals.
 Figure
7. The choice of termination resistors for a
transmission line depends on the
application.
Fail-SafeDeciding whether you need a
termination resistor or not is only part of the
problem in implementing an RS-485 system.
Normally, an RS-485 receiver output is "1" if A
> B by +200mV or more, and "0" if B > A by
200mV or more. In a half-duplex RS-485 network,
the master transceiver tri-states the bus after
transmitting a message to the slaves. Then, with
no signal driving the bus, the receiver's output
state is undefined, as the difference between A
and B tends towards 0V. If the receiver output,
RO, is "0," the slaves interpret it as a new
start bit and attempt to read the following
byte. The result is a framing error because the
stop bit never occurs. The bus goes unclaimed,
and the network stalls.
Unfortunately, different runs of chips can
produce different output signals on RO for a 0V
differential input. The prototype can work
perfectly, however, certain nodes will fail in a
later production run. To solve this problem,
bias the bus as shown in Figure 7 under
Multidrop/Fail-Safe Termination. Biasing the bus
ensures that the receiver output remains "1"
when the bus is tri-stated. Alternatively, you
can use "true fail-safe" receivers like those of
the MAX3080 (5V) and MAX3070 (3V) families.
These devices ensure an RO output of "1" in
response to a 0V differential input by changing
the receiver's threshold to -50mV.
RS-232/RS-485 Protocol TranslatorsThe
MAX3162 is an unique device for it contains both
RS-232 and RS-485 receivers and transmitters.
This wide range of communication devices
contained within a single IC enables an
individual to convert bidirectionally between
RS-232 and RS-485 signals. The circuit in
Figure 8 illustrates the MAX3162
configured to bidirectionally convert RS-232 and
RS-485 signals in a point-to-point application.
 Figure
8. The MAX3162 converts bidirectionally between
RS-232 and RS-485 signals in a point-to-point
application.
Figure 9 shows the MAX3162 configured
as an RS-232/RS-485 multipoint protocol
translator. The direction of translation is
controlled through the RTS signal, R1IN. The
single-ended RS-232 receiver-input signal is
translated to a differential RS-485 transmitter
output. Similarly, a differential RS-485
receiver-input signal is translated to a
single-ended RS-232 transmitter output. RS-232
data received on R2IN is transmitted as an
RS-485 signal on Z and Y. RS-485 signals
received on A and B are transmitted as an RS-232
signal on T1OUT.
The RTS line is a common means for
controlling bus direction in circuits that
convert from RS-232 to RS-485. This line on the
RS-232 port controls whether the RS-485
transceiver acts as a transmitter or a receiver
(Figure 9). Note that the system cannot be sure
that a byte of data in the UART's transmit
buffer has been transmitted unless the system
monitors the RS-485 driver input, DI. That is,
the system must either allow a fixed time delay
or actively monitor the DI input before using
the DE input to change the bus direction. Other
direction-control techniques include using a
microcontroller and driving the DE input with
data while pulling the A-B lines apart
(connecting a pull-up resistor from A to 5V and
connecting a pull-down resistor from B to
ground). The value of these resistors varies
with cable capacitance, but is typically 1k .
 Figure
9. The MAX3162 converts bidirectionally between
RS-232 and RS-485 signals in a multipoint
application.
Port-Powered DevicesMany converters
from RS-232 to RS-485 are "port-powered
converters" in which the RS-485 power is derived
from the RS-232 RTS line (or sometimes a
combination of the RTS and CTS (DTR) lines).
Because the power available from an RS-232 port
is limited, the RS-485 launch voltages are not
achieved when using a port-powered converter
with, for example, one hundred RS-485
terminations. The low receiver threshold
(200mV), however, allows a fair margin for
error. This technique is acceptable in systems
with short line lengths and without termination
resistors across the A-B terminals.
Hot-SwapWhen circuit boards are
inserted into a hot or powered backplane,
differential disturbances to the data bus can
lead to data errors. Upon initial circuit-board
insertion, the data communication processor
undergoes its own power-up sequence. During this
period, the processor's logic-output drivers are
high impedance and unable to drive the DE and
/RE\ inputs of the MAX3060E/MAX3080E to a
defined logic level. Leakage currents up to
±10mA from the high-impedance state of the
processor's logic drivers could cause standard
CMOS enable inputs of a transceiver to drift to
an incorrect logic level. Additionally,
parasitic circuit board capacitance could cause
coupling of VCC or GND to the enable inputs.
Without the hot-swap capability, these factors
could improperly enable a transceiver's driver
or receiver.
References
- RS-422 and RS-485 Application Note, B&B
Electronics (This is a great source of
information on RS-232, RS-485 and RS-422
standards and their practical realizations. http://www.bb-elec.com/)
- Serial Port Complete, Jan Axelson (This
definitive reference for serial ports includes
considerable useful source code written in
Visual Basic. http://www.lvr.com/)
We Want Your
Feedback! Love it? Hate it? Think it
could be better? Or just want to comment?
Please let us know—we act on customer
corrections and suggestions. Rate this page and provide
feedback.
Automatic
Updates Would you like to be
automatically notified when new application
notes are published in your areas of interest?
Sign
up for EE-Mail.
| More Information |
|
APP 723: Dec 29, 2000
|
| MAX232 |
+5V-Powered,
Multichannel RS-232 Drivers/Receivers |
Full
Data Sheet (PDF, 404kB) |
Free
Samples |
| MAX3162 |
+3.0V to +5.5V, 1µA,
RS-232/RS-485/422 Multiprotocol
Transceivers |
Full
Data Sheet (PDF, 588kB) |
Free
Samples |
| MAX3232 |
3.0V to 5.5V,
Low-Power, up to 1Mbps, True RS-232 Transceivers
Using Four 0.1µF External Capacitors |
Full
Data Sheet (PDF, 400kB) |
Free
Samples |
| MAX485 |
Low-Power,
Slew-Rate-Limited RS-485/RS-422
Transceivers |
Full
Data Sheet (PDF, 448kB) |
Free
Samples | |
|
Download, PDF
Format (104kB) AN723, AN 723, APP723,
Appnote723, Appnote 723
| |